Two potential problem areas -
1) If load generated switching noise you have to split grounds to make
sure load current does not generate IR drop logic signals back into PSOC
by raising a GPIO pin. As well large currents imply large magnetic fields,
so single turn loops created by layout practices create transformer coupling
back into GPIO. Additionally you can have e field coupling via parasitic C be-
tween load current traces and a GPIO pin. Where you can afford to burn power
terminate GPIO inputs in low Z to reduce coupling.
2) If relay actuator coil transients, generally speaking its relay coil turn off that produce
large transients. Make sure you have a reasonably fast diode across coil to handle
back emf. Diode must be rated for max coil I. DSO can be used to confirm diode
speed is clamping.